Post by andyb » Sat Jan 19, 2008 3:58 am

I am looking for reccomendations for a silent UPS, I have a few C&N UPS's at work and they buzz.

I cant live with a UPS at home that buzzes, whines, etc etc I dont even want one that has a fan in it if I can help it, please list me DONT's as well as Do's.

A couple of DO's and DONT's via these forums.

viewtopic.php?t=45748&highlight=ups
viewtopic.php?t=45384&highlight=ups

----

DO:

APC Smart UPS 750 (SUA750I) - see the unknown section below for the XL Model.
APC Back-UPS RS 800VA (UK 230v version owned and tested by me, more details in my post below - keep 3+ft away and its OK).
APC Back-UPS RS 1500VA (has a fan but it only runs when its running on battery - silent on mains).
Powerware 3110
MGE Ellipse MAX 1100VA
Belkin F6C525
APC BR500I (Back-UPS RS 500VA)
APC Smart-UPS SUA 750i
CyberPower Intelligent LCD Series GreenPower UPS CP1500AVRLCD

----

DONT:

APC Back-Ups XS900 (fan runs all of the time).
Belkin Universal UPS 1200VA
Belkin Dual Form Factor UPS 1500VA
APC Smart UPS SUA1500 (fan runs all of the time / constant high pitched noise)
APC Smart-UPS SUA 1500i: 1500VA

----

IFFY:

APC Smart-UPS 1500VA - Some people report this unit to have an always on fan, some say its silent/near silent. I will update this information as I get more information, it is possible that this unit is borderline due to heat or AC input voltage. I would suggest avoiding this unit at the moment.

----

UNKNOWN:

SmartUPS 750 XL (SUA750XLI) - The XL model's battery lasts 3x/4x longer, but at this time we dont know whether its a noisy beast, or just as quiet as the (SUA750I) - thanks to RPSGC.

----


The power draw of my server varies a little, but spends 90% of it time between 117W and 121W with the most common number being 119W, my 800VA unit will keep my server up for a long time (the APC Powerchute software says 40mins).

I will update the above list so that everyone can see what is and is not noisy in the UPS world.


Andy
Last edited by andyb on Sat Jan 09, 2010 6:16 pm, edited 14 times in total.

Das_Saunamies
*Lifetime Patron*
Posts: 2000
Joined: Tue May 15, 2007 1:39 am
Location: Finland

Post by Das_Saunamies » Sat Jan 19, 2008 4:24 am

Powerware 3110. About six or seven years old now, no fan and no buzz. If there is a sound, the whispering echo of my PC from two metres away drowns it out. :lol: (there is a sort of tickling sensation in my ear, like I was supposed to hear a sound, when I press my head close to the unit - but unless you sleep with it as a pillow in a 0dB environment, I doubt one notices it)

They no longer seem to sell it, so here's the current list: http://www.powerware.com/EMEA/UPS/EMEA_Products.asp

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Mon Jan 21, 2008 2:26 am

Thank you Das, that sounds good, the problem is that I have not seen anyone selling "Powerware" products in th UK, I wont be buying from eBay (ever), I wont buy from abroad, and ideally I would like to buy from a manufacturer who's replacement batteries can be found at a later date (if desired). The bottom line is that I have to skip your recommendation, thanks a lot for your help :)

I have had another power outage some time during the night, and the power is still not on (at least 4 hours so far). I am not looking for a UPS that can last out for that long, far from it - a few minutes will do. What I dont want is to buy a UPS that makes an annoying noise (any noise), and then have to buy another and another etc. Please add your suggestions.

I am currently looking at an APC Back-Ups RS 800VA 230V (AKA BR800I), its battery back up time will be fine for my needs and its only £90 including Tax. It is in the same range as a recommended UPS which is good, as the SPCR'er in question states that it is silent in general use, and its fan only runs when it is using the battery. The bad news is that it has a fan, and the UK version may be different from the US version (different AC voltage), also I found a product manual for the RS and the XS, which is a non-recommended product which would suggest that there is not a huge amount of difference between the two models.

http://www.apc.com/resource/include/tec ... sku=BR800I
http://www.apcmedia.com/salestools/ASTE ... _R0_EN.pdf


Andy

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Mon Jan 21, 2008 5:03 am

Ordered, I will let you all know if its noisy tomorrow.

http://www.apc.com/resource/include/tec ... sku=BR800I


Andy

_MarcoM_
Posts: 294
Joined: Thu Jul 21, 2005 11:58 am

Post by _MarcoM_ » Mon Jan 21, 2008 6:54 am

Nice UPS andyb, wanna buy one for my rig. Let me know if there are troubles with Active PFC, don't want to burn my new power supply :?

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Mon Jan 21, 2008 8:43 am

Let me know if there are troubles with Active PFC, don't want to burn my new power supply
I would be amazed if there were any problems, the vast majority of PSU's use Active PFC now, (I would guess 80+%). I will let you know if I have any problems at all.


Andy

_MarcoM_
Posts: 294
Joined: Thu Jul 21, 2005 11:58 am

Post by _MarcoM_ » Thu Jan 24, 2008 12:12 pm

Any news? :)

aristide1
*Lifetime Patron*
Posts: 4284
Joined: Fri Apr 04, 2003 6:21 pm
Location: Undisclosed but sober in US

Post by aristide1 » Thu Jan 24, 2008 2:11 pm

UPS's must work with APFC PS. APFC is mandated in Europe. Correct?

frostedflakes
Posts: 1608
Joined: Tue Jan 04, 2005 4:02 pm
Location: United States

Post by frostedflakes » Thu Jan 24, 2008 2:31 pm

I use an APC Back-UPS ES 350VA and never had any problem with active PFC power supplies. Then again, I rarely run my PC off it for extended periods of time (especially considering I can only get about five minutes battery life out of it). I mainly got it for power spikes and brief losses, it's such a pain to lose all of your work because the power went out for a split second.

As far as noise goes, it's silent (to my ears, at least) when charging and not running on battery. However, when running on battery power it does buzz slightly. It's not anything obtrusive, though, you have to get within a foot or two of the unit to really hear it.

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Fri Jan 25, 2008 7:17 am

My UPS makes a horrible electrical buzzing noise that seems quite loud when up close, however it seems to vanish very quickly with a little distance. 2ft away it is barely audible, 3ft it is inadable in a quiet environment but may still be audible in <22Db environments at this distance, longer power cables can easily be used and the USB data cable to shut it down via software can be a maximum of 5M.

When it is running off of the battery, the noise becomes far louder, and it is very audible even from 5-6ft away in a noisy environment.

Notes: It has no fan, it has 4 power sockets that are battery protected and a further 2 that are surge protected. It also has surge sockets for telephone and network cables. All 6 of the power sockets are female IEC connectors, 2 cables supplied, the cable type on the right of the picture linked below.

http://www.dansdata.com/images/io017/cables500.jpg


Andy

_MarcoM_
Posts: 294
Joined: Thu Jul 21, 2005 11:58 am

Post by _MarcoM_ » Fri Jan 25, 2008 4:17 pm

Uhm, weird, maybe your BR800I unit is defective, electrical buzzing noise is not present in the model Back-UPS Pro 650, and BR800I is the successor of this one.

Das_Saunamies
*Lifetime Patron*
Posts: 2000
Joined: Tue May 15, 2007 1:39 am
Location: Finland

Post by Das_Saunamies » Sat Jan 26, 2008 5:01 am

Successors don't always make things better. :wink:

Too bad it turned out poor, APC is a lot more widespread than Powerware. Powerware does have distributors in the UK tho', in case you want to give them a try: http://www.powerware.com/how_to_buy/reseller.asp

Sorry I didn't respond sooner, was cut off for a week or so.

jaganath
Posts: 5085
Joined: Tue Sep 20, 2005 6:55 am
Location: UK

Post by jaganath » Sat Jan 26, 2008 7:50 am

APFC is mandated in Europe. Correct?
PFC is mandatory but it can be passive or active, very cheap PSUs only have passive.

_MarcoM_
Posts: 294
Joined: Thu Jul 21, 2005 11:58 am

Post by _MarcoM_ » Sat Jan 26, 2008 2:15 pm

Das_Saunamies wrote:Successors don't always make things better. :wink:
Ehhh, sadly true :(

CoolGav
Posts: 398
Joined: Wed Jul 23, 2003 4:26 am
Location: €ngland
Contact:

Post by CoolGav » Tue Jan 29, 2008 7:41 am

I have an APC Smart-UPS 750. I'm not sure if it makes a little noise or not as it's in my loft with my server. I can't recall it being any noisier than the server (which is not too loud) - perhaps I'll be able to take a close listen soon...

_MarcoM_
Posts: 294
Joined: Thu Jul 21, 2005 11:58 am

Post by _MarcoM_ » Tue Jan 29, 2008 12:14 pm

CoolGav wrote:perhaps I'll be able to take a close listen soon...
Yes, please :)

AntecRep
-- Vendor --
Posts: 184
Joined: Tue Jan 21, 2003 7:15 am
Contact:

Buzz Buzz

Post by AntecRep » Tue Jan 29, 2008 2:07 pm

Square-waves and active PFC don't play well together. If you don't want buzz, then make sure UPS output is sine-wave. Some UPSs will not buzz when getting power from the wall, but make a racket when powering from battery.

aristide1
*Lifetime Patron*
Posts: 4284
Joined: Fri Apr 04, 2003 6:21 pm
Location: Undisclosed but sober in US

Post by aristide1 » Tue Jan 29, 2008 2:37 pm

jaganath wrote:What do our opponents mean when they apply to us the label "Liberal?" If by "Liberal" they mean...someone who looks ahead, who welcomes new ideas without rigid reactions,who cares about the welfare of the people, who believes we can break through the stalemate and suspicions that grip us in our policies abroad...then I'm proud to say I'm a "Liberal."
Well, the decline of professional civility started with Ronald Reagan and his little funky pronunciations of Massachusetts, like that was a dirty word in and of itselt. Ironically enough his home state contains Hollywood, and we all know what that means.

It's hard to believe that just a couple of decades ago pubs and dems would carpool to work together, argue the issues at work, and, at the very least, then actl like rational human beings when the shift was over. Today, in the 21st century, you have eldery (can't use the word mature) bigots behaving like spoiled brats, their mention appears to be Dennis Miller or Ann Coulter.

Which leaves me once again with the unanswered question.
Who is the democratic equivalent of?

Ann Coulter?
Rush Limbaugh?
Dennis Miller?

The lack of answer implies that the dems don't use hate mongers. I don't know, is that the case?

walle
Posts: 605
Joined: Tue Dec 26, 2006 10:52 am

Post by walle » Tue Jan 29, 2008 2:53 pm

I’ve missed this thread previously, well; glad I found it because I’m in the market myself for a silent UPS. Andyb, do you still have issues with the unit? or have you replaced it even? I’m asking because I’ve been eyeballing the very same unit.

Thanks.

Rinswind
Posts: 11
Joined: Thu Aug 23, 2007 6:20 am
Location: Sofia, Bulgaria

Post by Rinswind » Fri Feb 01, 2008 2:34 am

Is this thread still alive?
I'm looking for a silent UPS myself. It is critical that it be inaudiable because i'll be sleeping about 3 feet from it. And you know how even the slightest noise becomes a real nuisance at hight :)

So far I'm looking at 3 models. I'm listing them in order of preference:
1) MGE Ellipse Max 1100VA
2) MGE Evolution 1000VA
3) APC Smart UPS XL 1000VA

Does anywaone have any experience with the Ellipse?

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Fri Feb 01, 2008 7:42 am

walle, I would be happy to recommend the same unit that I have so long as you are not too close, I have it under a desk about 4ft away from me, and I cant hear it at all.

Rinswind, I would not recommend this unit if you are going to be within 3ft of the unit, especially at night in a quiet environment. Long power and USB cables are available, so you could have the unit some distance away if you dont find a more suitable candidate.


Andy

walle
Posts: 605
Joined: Tue Dec 26, 2006 10:52 am

Post by walle » Fri Feb 01, 2008 9:28 am

Ok, thanks for the answer and feedback Andyb, much appreciated.

Cheers.

CoolGav
Posts: 398
Joined: Wed Jul 23, 2003 4:26 am
Location: €ngland
Contact:

Post by CoolGav » Mon Feb 04, 2008 8:11 am

_MarcoM_ wrote:
CoolGav wrote:perhaps I'll be able to take a close listen soon...
Yes, please :)
My server is next to the UPS (APC Smart-UPS 750), and has a few 120mm Antec fans, so not a silent listening area, but I couldn't hear it making any buzz or whines. There isn't any active cooling on it either - I've just set it up and it does it's thing...

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Mon Feb 04, 2008 8:24 am

I had a listen to my UPS last night (1-AM) after I had turned my server off.

On my hands and knees under my desk, with the UPS 4ft away to my left, my uber-silent PC made the same volume of noise 1-ft away to my right.

My PC is very very quiet, utterly inaudable from my chair the UPS can be heard over it from 3ft, a crackly, electrical buzzing.

As mentioned before this is not really an issue unless someone is very sensitive to this kind of noise, or they have the UPS within a short distance, or their environment is even quieter than mine. I hope this helps. As far as how much noise my PC actually makes, it is not easy to tell without pro level equipment, but judging by SPCR's reviews on the Nexus fans @5v the answer is <20Db, my HDD can not be heard over the noise of whooshing unless there is a lot of long seeks going on (rarely). To give another perspective I can hear my neighbours hot water being pumped around and their boiler boiling over my PC from 1ft. :P


Andy

Tzupy
*Lifetime Patron*
Posts: 1561
Joined: Wed Jan 12, 2005 10:47 am
Location: Bucharest, Romania

Post by Tzupy » Mon Feb 04, 2008 10:03 am

@CoolGav: could you please tell us if this is the APC Smart UPS that you have?
http://www.apcc.com/resource/include/te ... ku=SUA750I
According to the specification, audible noise at 1 meter from surface of unit is 55dBA!!!

_MarcoM_
Posts: 294
Joined: Thu Jul 21, 2005 11:58 am

Post by _MarcoM_ » Mon Feb 04, 2008 11:42 am

andyb wrote:I had a listen to my UPS last night (1-AM) after I had turned my server off.

On my hands and knees under my desk, with the UPS 4ft away to my left, my uber-silent PC made the same volume of noise 1-ft away to my right.

My PC is very very quiet, utterly inaudable from my chair the UPS can be heard over it from 3ft, a crackly, electrical buzzing.
IMO it's a defective UPS: i expect noise under battery-mode, but there is not reason to make noise under normal condition. My friends, any opinions about this point?

andyb
Patron of SPCR
Posts: 3307
Joined: Wed Dec 15, 2004 12:00 pm
Location: Essex, England

Post by andyb » Mon Feb 04, 2008 2:00 pm

My server is now on, which is 6 inches to my right ear, I can barely hear the UPS 4 inches to my left ear. My server is probably in the region of 24Db - 27Db.

I hope this helps.


Andy

CoolGav
Posts: 398
Joined: Wed Jul 23, 2003 4:26 am
Location: €ngland
Contact:

Post by CoolGav » Tue Feb 05, 2008 9:06 am

Tzupy wrote:@CoolGav: could you please tell us if this is the APC Smart UPS that you have?
http://www.apcc.com/resource/include/te ... ku=SUA750I
According to the specification, audible noise at 1 meter from surface of unit is 55dBA!!!
Yes, that's the one - I'm not too worried about it's noise as it's in my loft. I'm not really able to comment on their 55dBA, perhaps it's when on battery...

Rinswind
Posts: 11
Joined: Thu Aug 23, 2007 6:20 am
Location: Sofia, Bulgaria

Post by Rinswind » Tue Feb 05, 2008 9:55 am

I wrote to APC asking about the noise of the Smart family and this is their replay about the line-interactive Smart XL 1000VA unit:

"If you check the product specification sheet on our website from the following link, we says that the audible noise at 1 meter from surface of the unit is 42 dBA

http://www.apc.com/resource/include/tec ... sua1000xli

In that unit the fan is running when the UPS is operating from the battery, when charging the Battery and when the internal temperature of the UPS is more than 36 C."

This is their reply about the online Smart RT 1000VA unit:

"For the SURT1000XLI the value is 50 dBA.

http://www.apc.com/resource/include/tec ... urt1000xli

The fan in SURT1000XLI is running all the time."

An finally about 1000VA units in general:

"There is no silent unit for the range of 1000VA."

So I guess this means that if you have your unit fully loaded and manage to keep the internal temperature below 36 C things should be relatively silent?

CoolGav you said you could not hear buzzing or humming from it. I guess you weren't listening during a blackout and since it's winter in europe your experience should fit these "silent" conditions right? :)

Another interesting point is that you say your Smart XL 750VA has no active cooling. However APC say the 1000VA variant has some fan and as far as I can tell from the link above the 1000VA and 750VA seem practically identical. I guess the fan is not visible from outside.

Rinswind
Posts: 11
Joined: Thu Aug 23, 2007 6:20 am
Location: Sofia, Bulgaria

Post by Rinswind » Sun Feb 17, 2008 5:52 am

Calling to report I chose convenience and bought the MGE Ellipse MAX 1100VA unit. It is almost absolutely silent: While it was charging the battery it emitted a very high pitched whine which one has to listen carefully to make out. Once the battery charged I can hear a slight buzz only when I press my ear to the unit. I spent my 3-rd night near it just now and had no complains :)

The distributor for my country said the waveform this one outputs is a "smoothed trapezoid". I guess this means they smooth the sharp edges to make it easy on the PSU. Anyway my Corsair HX520 does not emit any unusual whines while on battery.

It is rather light (10.2 kg) however it claims to be able to support the system from my signature for about 40 minutes. It reports a load of 10-17% as I write this post, listen to an mp3 and have my torrent client upload to about 100 connections. I also have my Linksys WRT54GL router supported by the battery.

So far I can't ask for anything more - we'll see how it performs during the next blackout :)

Post Reply